Good info guys. I did some surfing on the net and what I did is called flat venting. It will probably work but it is against code. Eventually that line will have build up and restrict the airflow.
I will now cut into the 2” line right after the trap and bring a vent in between the 10 & 2 o’clock position. That way the vent is above the water line in the pipe.
Do you agree on this change?
Thanks for all that have given me guidance and on this project. That’s what makes this site so awesome!